What is the general rule of thumb for pressure testing a Hep2O system?

In all cases you should carry out a low pressure test at 0.5-1 bar. If the system is just demountable fittings, pressure test at 1.5x working pressure with a recommended minimum of 10 bar for minimum 45 mins. 