What maintenance is required when installing a HepvO valve in a discharge from an unvented hot water cylinder?

There is no specific maintenance requirement especially for HepvO in this application. Unvented systems should be inspected at intervals not exceeding 12 months, and during this inspection the safety valves & discharge pipe should be checked for correct operation, i.e. no blockage. This would indicate that HepvO is also functioning.